Worked examples: choke on the mains, and an 11 kV → 230 V transformer
AC Circuits · Inductive Reactance · Example
Three problems. First: X_L for a real choke on 50 Hz mains, and how it changes at 20 kHz. Second: a magnetism sanity check — find B inside an iron-cored solenoid. Third: size a distribution transformer the way a protection engineer does, then verify with the playground.
Example 1 — 100 mH choke on 50 Hz mains vs 20 kHz SMPS
A 100 mH iron-cored choke sits in series with a 230 V RMS 50 Hz mains supply through a 10 Ω resistor. Later the same choke is re-used on the output of a switching power supply running at 20 kHz. Find X_L at each frequency and the current it limits.
- Reactance at 50 Hz.Comparable to the 10 Ω resistor in series, so the choke significantly limits mains-frequency current.
- Approximate RMS current. Ignore the resistor's phase contribution for a quick estimate (we'll do this properly once we reach impedance in Topic 8):.
- Reactance at 20 kHz (400× higher).Four hundred-fold jump. A choke that barely troubled 50 Hz mains looks like a near-open at SMPS frequencies — exactly what you want in a power-supply filter.
At the marked frequency
Drag the frequency marker to 20 kHz and watch the line climb by 2.6 decades. Move the inductance slider down to 1 mH and the line slides down by two decades — all the qualitative rules about chokes fall out of that one sweep.
Example 2 — B inside an iron-cored solenoid
A solenoid has turns wound on an iron core long. Relative permeability (typical for silicon steel). The coil carries 0.5 A. Find the magnetic field intensity H, the flux density B, and the total flux Φ through a 1 cm² cross-section.
- Field intensity H.
- Flux density B.Hot — real iron saturates around 1.5 – 2 T, so a practical design would either drop the current or accept that the core is now deep in saturation and collapses. The formula still works; it just stops telling the truth once the iron gives up.
- Total flux Φ through 1 cm².(Again, pre-saturation value — real core would give roughly 150 – 200 µWb after saturation takes hold.)
Example 3 — Distribution transformer: 11 kV → 230 V
A step-down distribution transformer takes an 11 kV primary down to 230 V for domestic use. If the primary has 2 000 turns, how many turns are on the secondary? Under a 10 kW load on the secondary, what currents flow on each side (treat as ideal)?
- Turns ratio from voltage ratio.So turns. Dozens, not thousands — the secondary is a short, fat winding of thick wire.
- Secondary current under load.That's why the low-voltage winding needs chunky copper.
- Primary current (ideal).Same power, 50× less current — the whole reason we transmit at high voltage.
Example 3 — operating point snapshot
Push V₁ to 400 V (the widget caps there — only the ratio matters), N₁ = 2000, N₂ ≈ 40, and raise P to scale the currents up. You'll see the primary draw ~50× less current than the secondary at every load — the rationale for high-voltage transmission.
Open playground →Sweep your own values in the Simulate stage or lock in the reflex on the Quiz.